What is the installation specification for the electromagnetic flowmeter?
1/7/2019 9:12:55 AM
1. Keep away from strong magnetic field equipment.
2. Avoid strong vibration and strong corrosive places.
3. The process does not allow the flow of the pipeline to be interrupted. When installing the flowmeter, a shut-off valve and a bypass line should be added.
4, the upstream of the flowmeter sensor should also have a certain straight pipe section, generally in 5D~10D.
5, can be installed horizontally, vertically and obliquely, but to ensure that the measuring tube is coaxial with the process pipe, and that the measuring tube is always filled with liquid.
6, the sensor's measuring tube, the outer casing, the shield wire of the lead, and the pipe at both ends of the sensor must be reliably grounded, and must not be shared with the grounding of other electrical equipment, which is the special installation requirements of the electromagnetic flowmeter.